Festo CVE-2022-22515 and CVE-2022-31806: Risk in Vision System Controllers

  • Thread Author
A coordinated security advisory has exposed high-severity weaknesses in a broad range of Festo products — including the Compact Vision System, multiple Control Block and Controller SKUs, and several Operator Unit models — that can allow remote attackers to read and modify configuration files or gain unauthenticated access when insecure defaults are present. The two headline findings map to CVE‑2022‑22515 (a Codesys runtime control‑program configuration‑file disclosure/modification issue) and CVE‑2022‑31806 (an unsafe default in CODESYS V2 runtime that leaves password protection disabled), and both carry high CVSS scores that demand immediate operational attention from OT and converged IT/OT teams.

A hooded figure in a dark server room monitors red CVE alert screens.Background / Overview​

Festo’s automation portfolio — spanning embedded controllers, control blocks, vision subsystems and operator panels — is widely deployed inside machine control cabinets and on industrial networks. These devices frequently sit at the IT/OT boundary, reporting telemetry to PLCs and supervisory systems or exposing management interfaces for vendor maintenance. That placement makes any remote‑accessible vulnerability particularly consequential: a compromised unit can be an entry point for lateral movement, data exfiltration, or direct manipulation of machine state. The coordinated disclosure includes vendor advisories and a national CERT advisory that emphasize network exposure as the primary operational risk lever.
Festo’s published CSAF advisory and the coordinating national advisory outline two related but distinct problems:
  • A Codesys runtime control‑program weakness (tracked as CVE‑2022‑22515) that allows a remote, authenticated attacker using the Codesys Control runtime control program to read and alter device configuration files.
  • An insecure default in certain CODESYS V2 runtimes (tracked as CVE‑2022‑31806) where password protection is not enabled by default and users are not prompted to set it — enabling unauthenticated or trivially authenticated access when devices remain at factory defaults.
Together these issues raise the likelihood of unauthorized configuration changes, credential theft, and persistence on affected devices — outcomes that can quickly escalate into safety and availability incidents in manufacturing environments.

Affected products (high‑level)​

Festo’s advisory enumerates a broad list of affected SKUs across product families. Rather than reproduce an exhaustive SKU table in this article, note the inclusive pattern the vendor used: many Compact Vision System, Control Block, Controller, and Operator Unit models are listed as "All Versions" for their respective SKUs in the advisory. Representative affected categories include:
  • Compact Vision System SBO‑Q family.
  • CPX‑CEC / CPX‑CEC‑C1 / CPX‑CEC‑M1 control block variants (Codesys V2 and V3 bundles).
  • CECC‑, CECX‑, CPX‑E‑CEC* controller families across multiple variants.
  • Multiple CDPX operator unit models (touch and display variants).
Operators should treat any machine that contains the listed families as in‑scope until device inventory records confirm otherwise. The advisory marks all versions of the listed SKUs as affected, meaning firmware or hardware revision alone is not a safe assumption of remediation.

Technical details: what the vulnerabilities actually allow​

CVE‑2022‑22515 — Codesys control program abuse (read/modify configuration)​

  • What it is: A weakness in the CODESYS Control runtime control program allows a remote, authenticated actor to read and modify configuration files used by the affected devices. Once configuration files are altered, attackers can change device behavior, extract secrets, or drop malicious assets that persist across reboots.
  • Attack prerequisites: Network reachability to the Codesys control interface and at least low‑privileged authentication (the advisory notes low privilege is sufficient in many cases). The practical implication: if any accessible account or default credential is present, the attacker can escalate the impact.
  • CVSS and impact: The issue was assigned CVE‑2022‑22515 with a vendor/coordination CVSS v3.1 base score reflecting high confidentiality and integrity impact (vendor scoring placed it in the high severity range). Successful exploitation yields the ability to alter control programs or device configuration — directly undermining process integrity.

CVE‑2022‑31806 — Unsafe CODESYS V2 default (no password)​

  • What it is: In some CODESYS V2 runtime builds (for example, PLCWinNT and Runtime Toolkit 32 prior to certain versions), password protection is not enabled by default and users are not prompted to set a password at first login. That means devices shipped or reset to factory defaults can be accessible without authentication until administrators proactively set passwords.
  • Attack vector and severity: Because the weakness removes the barrier of authentication, the advisory assigns this issue a very high CVSS score (reported as 9.8 in vendor/coordination scoring); it is trivially exploitable if the device is network reachable. An attacker with network access can log in to an unprotected controller and perform administrative actions, including firmware/configuration changes and command execution.

Combined risk model​

When combined, these two issues materially lower the bar for both reconnaissance and full compromise:
  • A device with an unsafe default password setting is effectively unauthenticated, which lets an attacker reach the Codesys control program and then leverage CVE‑2022‑22515 paths to read/modify configurations.
  • Because many affected SKUs are embedded components in machines, a single compromised device can result in manipulation of valve states, setpoints, or telemetry, and provide a foothold for lateral movement into engineering or business networks if segmentation is weak.

Vendor and coordinating‑CERT findings, and what was reported publicly​

Festo coordinated disclosure and published a security advisory describing the affected product list, the nature of the unsafe defaults, and recommended mitigations centered on enabling password protection and minimizing network exposure. The advisory also identified that the default FFT backup & restore mechanism does not include the password configuration file — administrators must select the file manually to protect password settings during backup/restore operations.
The national coordinating advisory emphasizes that no public exploitation had been reported to that authority at the time of publication, but warns that no known exploitation is a transient status; the combination of remote accessibility and low attack complexity means the practical window for attack is large once exploit details are public. Operators were urged to assume devices are at risk until mitigations are in place.

Mitigations and compensating controls (vendor + CISA guidance synthesized)​

Festo and CISA provided overlapping mitigation guidance. The key operational controls — prioritized and translated into an actionable checklist — are:
  • Disable or restrict remote network exposure immediately:
  • Ensure management interfaces for affected devices are not internet‑reachable.
  • Place affected units behind firewalls that restrict access to specific engineering jump hosts or vendor maintenance addresses.
  • Enable password protection now:
  • For devices running CODESYS V2 where password protection is not enabled by default, administrators must enable password authentication immediately. Remember that password configuration files may not be included in default backups and must be selected during FFT backup & restore.
  • Use secure remote access:
  • If remote access is required, use up‑to‑date VPNs or vendor remote access platforms that implement strong authentication and authorization controls. Recognize that VPNs are not a panacea and must themselves be kept patched and restricted.
  • Apply least privilege and credential hygiene:
  • Rotate vendor and maintenance credentials, remove default accounts, enforce unique, complex passwords, and restrict administrative privileges. Audit service and maintenance accounts for unnecessary global rights.
  • Compensating documentation/workarounds:
  • Festo notes that using online user management can prevent code download/execution paths but may also block legitimate start/stop/debug actions on known, working applications; operators must weigh operational impact vs. security needs and perform change control accordingly.
  • Monitor and detect:
  • Increase logging and network monitoring for unusual activity targeting management ports, unexpected configuration downloads, or unauthorized code‑upload attempts. Treat any unexpected configuration change as a high‑priority incident.

Operational playbook: step‑by‑step actions for the first 72 hours​

  • Inventory: Identify all devices matching the affected families (Compact Vision System, CPX/CECC/CECX controllers, CDPX operator units, etc.. Prioritize devices with public IPs, remote maintenance tunnels, or known flat network placement.
  • Isolate: For any affected device reachable from the internet or across network segments, remove or block access (apply firewall rules, move to a quarantined OT VLAN).
  • Password enforcement: For any device running an affected CODESYS V2 runtime, immediately ensure password protection is enabled. Confirm that password configuration files are backed up manually if using FFT backup & Restore.
  • Credential hygiene: Disable or rotate default/maintenance credentials, and replace shared accounts with individual accounts scoped to least privilege.
  • Compensating settings: If practical, enable online user management (noting it may suppress some runtime operations) or otherwise restrict actions like remote application start/stop/debug to vetted maintenance windows.
  • Monitor: Implement enhanced logging, IDS/IPS rules for Codesys control ports, and host integrity checks to detect unauthorized configuration changes.
  • Patch & change management: Review vendor channels for any firmware or software updates, but do not apply invasive changes without impact analysis; many ICS sites require careful testing and downtime coordination. If vendor patches are provided, validate in a testbed before plant deployment.

Detection and response: indicators and forensic steps​

  • Indicators of compromise (IoCs) to watch for:
  • Unexpected modifications to project or configuration files on controllers.
  • New or changed accounts on CODESYS runtimes.
  • Network traffic to and from management ports (CODESYS control ports) from unusual IP ranges.
  • Forensic steps after suspected compromise:
  • Preserve volatile logs and extract configuration file snapshots before remediation to support root cause analysis.
  • Capture network flows that include interactions with management interfaces during the suspected window.
  • Compare current configuration files against known good backups to identify unauthorized changes.
  • Recovery considerations:
  • Rebuild controllers only from known good images where possible; do not rely on backups that may themselves have been tampered with unless they are validated.
  • Rotate credentials and review connected systems for lateral movement.

Why this matters: risk to critical manufacturing and downstream systems​

These vulnerabilities are not just a theoretical risk to isolated devices. The advisory deliberately calls out critical manufacturing and similar sectors where a control device’s compromise can have immediate operational and safety consequences. The blast radius depends on network architecture: in well‑segmented OT environments, a compromise can often be contained locally; in flat or poorly segmented networks, an attacker can pivot to PLCs, historians, engineering workstations, or even safety systems. The advisory’s urgency stems from two practical factors: (1) remote exploitability combined with low attack complexity, and (2) the insecure default behavior in some runtimes that removes the authentication barrier entirely.

Strengths and limits of the vendor response (critical analysis)​

Strengths:
  • Festo coordinated disclosure with a national coordinating authority and published a detailed advisory listing affected SKUs and mitigations; that coordination is positive and consistent with responsible disclosure practices.
  • The advisory emphasizes network isolation and password enforcement — high‑impact compensating controls that operators can apply without waiting for firmware revisions.
Potential weaknesses and risks:
  • The vendor’s immediate remediation guidance for one class of issues centers on procedural changes and documentation updates (for example addressing undocumented/test functions or defaults) rather than shipping a universal firmware fix that closes the vulnerability by design. That means many sites will be dependent on operational compensations, increasing the burden on defenders and creating opportunities for human error during long remediation windows.
  • The advisory highlights that the password configuration file is not covered by default backup flows, which raises the risk that administrators who perform backups without manual file selection will restore configurations that leave devices unprotected. This gap is a practical operational risk that must be explicitly addressed in change control procedures.
  • The practical dependence on administrators to discover and remediate affected devices means coverage will vary by organization; if inventories are incomplete or remote maintenance tunnels are unmanaged, exposure persists.
Caveat on exploit reporting:
  • At the time of the advisory publication the coordinating authority reported no known public exploitation; that is important but ephemeral — defenders should treat it as a status snapshot, not a guarantee of future safety.

Longer‑term recommendations and security posture improvements​

Beyond immediate containment, industrial organizations should treat this advisory as a prompt to accelerate these longer‑term improvements:
  • Inventory and asset management: Maintain an accurate, continuously updated inventory of embedded devices, including firmware versions and management interface exposure. Use automated asset discovery tools where possible.
  • Network design for OT: Enforce strict segmentation between OT and IT, limit east‑west traffic in OT subnets, and apply allow‑lists for maintenance traffic rather than broad remote tunnels.
  • Secure default configuration: Demand secure‑by‑default devices from vendors — critical defaults must include enforced password setup and minimal exposed services. Incorporate secure‑default requirements into procurement contracts and vendor acceptance tests.
  • Patch management and testbeds: Establish testbed procedures for validating vendor firmware and software updates before deployment into production control systems. Prioritize fixes for issues with high CVSS and network reachability.
  • Incident preparedness: Develop and rehearse an OT‑specific incident response plan that includes forensic collection for controllers and procedures for safe system rebuilds.

Unverifiable or open items (cautionary notes)​

  • Public exploitation: Multiple coordinating notices stated no confirmed public exploitation at publication time, but that status can change quickly. Treat the absence of reported exploitation as temporary and respond proactively.
  • Exact remediation timelines: Some vendor remediations for related product classes have been documentation updates rather than immediate firmware changes; where a code‑level patch is not available, operators must rely on compensating controls. Organizations should verify the vendor’s product roadmaps and requested update schedules for each affected SKU.

Conclusion​

The Festo advisory covering the Compact Vision System, Control Block, Controller, and Operator Unit families highlights two interlocking vulnerabilities that significantly raise operational risk when devices remain network‑exposed or at factory default settings. CVE‑2022‑22515 allows authenticated misuse of the Codesys control program to read and change configuration, while CVE‑2022‑31806 describes an unsafe default that can leave devices unprotected without immediate administrative action. The path to risk reduction is straightforward in principle — inventory affected devices, remove internet exposure, enable password enforcement, rotate credentials, and apply strict segmentation — but execution in live industrial environments requires coordination, testing and disciplined change control. Treat this advisory as an urgent operational priority: apply the mitigations now, validate backups and authentication settings, harden your OT network design, and prepare for detection and response if signs of compromise appear.


Source: CISA Festo Compact Vision System, Control Block, Controller, and Operator Unit products | CISA
 