In the intensifying race to minimize the environmental impacts of global cloud infrastructure, Microsoft's newly published study in Nature marks a pivotal advancement for data center sustainability. For the first time, researchers have provided a comprehensive, cradle-to-grave life cycle assessment (LCA) that quantifies the energy, water consumption, and greenhouse gas (GHG) emissions of four major data center cooling techniques: air cooling, cold plates, one-phase immersion, and two-phase immersion. This research not only narrows a critical knowledge gap but also proposes methodologies and tools for industry-wide adoption, paving the way for more eco-conscious facility design, construction, and operation.

A futuristic server room features illuminated racks with cooling fans and plants in water-filled containers.
Understanding the Scope: Life Cycle Assessment in Data Centers​

Data centers are the backbone of modern digital society, but their environmental toll is significant and growing. Most previous analyses of their sustainability have focused only on operational impacts—energy and water consumed during use. What sets Microsoft’s Nature study apart is its holistic approach: the team analyzed emissions and resource use starting from raw material extraction, through manufacturing and transport of hardware and cooling systems, to end-of-life disposal. This "cradle-to-grave" perspective captures subtler environmental burdens, such as those associated with manufacturing chips, constructing cooling equipment, and even the water used for power generation.
According to Husam Alissa, Microsoft’s director of systems technology, “[a] lot of people do life cycle assessments after the fact,” but using LCAs as a design tool enables earlier, data-driven decisions that can fundamentally lower the ecological footprint of future data centers. Notably, Microsoft is advocating for, and sharing, their LCA methodology as an open resource, aiming to help others in the industry reduce energy, water, and GHG emissions.

Cooling the Cloud: Technologies Under Review​

The study scrutinizes the environmental impacts of four cooling techniques:
  • Air Cooling: The standard, long-time method involving pumps and fans to dissipate heat.
  • Cold Plate Cooling: Coolant fluid circulates within plates that sit directly atop data center chips, greatly improving heat transfer efficiency.
  • One-Phase Immersion: Servers are submerged in a tank where a cooling fluid flows in a circuit, removing heat efficiently.
  • Two-Phase Immersion: Servers are immersed in a fluid which boils at a low temperature; the resultant vapor is condensed and cycled, leveraging the latent heat of vaporization for cooling.
While liquid cooling techniques have drawn attention for their potential efficiency, Microsoft's study is notable for quantifying, rather than simply theorizing, their advantages and trade-offs throughout the hardware’s lifespan.

Key Findings: Carbon, Water, and Energy Comparisons​

Microsoft’s LCA reveals that switching from air cooling to cold plates, or the two immersion methods, can reduce overall GHG emissions by 15–21%, energy demand by 15–20%, and water use by an impressive 31–52% over the full life cycle of a data center. Importantly, these figures include not just operational consumption, but all embedded impacts: manufacturing servers, producing cooling equipment, and even the energy mix used by the local grid.
The analysis also found that switching to 100% renewable energy in data center operations—regardless of chosen cooling technology—can reduce greenhouse gas emissions by 85–90%. However, the full water and energy savings of advanced cooling become most pronounced when combined with greener energy sources.

Breakdown by Cooling Technology​

TechnologyGHG ReductionEnergy Demand ReductionWater Use Reduction
Air CoolingBaselineBaselineBaseline
Cold Plate~15%~15%30–50%
1-Phase Immersion15–21%15–20%31–52%
2-Phase Immersion15–21%15–20%31–52%
Values are approximate, lifecycle averages, and subject to detailed assumptions as outlined in the Nature paper.
It's important to highlight that the detailed results depend on precise design choices and life cycle boundaries—parameters such as cooling system lifetime, regional energy mixes, and component manufacturing sources can significantly affect outputs. As the authors note, these results may shift with evolving technologies and regional factors.

Cold Plates: A Near-Term Path to Sustainability​

Of the liquid cooling options studied, cold plates represent the most immediately deployable advancement over air cooling. Because they bring coolant directly into contact with server chips, cold plates offer several benefits:
  • Direct Heat Dissipation: More efficient removal of heat translates to lower fan speeds and less power consumption.
  • Lower Water Use: Water is used not just for cooling, but in ancillary processes such as power generation and chip manufacturing. Cold plate systems show a substantial reduction in this cumulative demand.
  • Retrofittable Design: Cold plates are compatible with existing server racks, easing transitions compared to more radical immersion systems.
Microsoft is already deploying cold plate cooling in some of its largest data centers, and the company attributes the decision to this technology’s proven GHG and water savings over conventional air cooling.

The Promise and Peril of Immersion Cooling​

One-Phase Immersion​

In one-phase immersion, servers operate submerged in an electrically non-conductive fluid. The simplicity and effectiveness of this approach—single fluid, single phase—results in considerable GHG and water savings, though deployments remain limited, largely due to logistical challenges and compatibility requirements for server hardware.

Two-Phase Immersion: Efficiency and Environmental Risks​

Two-phase immersion offers arguably the highest theoretical cooling efficiency, since vaporization absorbs more heat per gram of fluid. But the Nature study raises critical caveats: the fluids commonly used are polyfluoroalkyl substances (PFAS), which remain persistent in the environment and are under heightened regulatory scrutiny in both the US and EU. Some reports suggest PFAS bans could severely curtail future use of two-phase immersion fluids, potentially undermining the technology’s sustainability case despite its energy benefits.
Microsoft confirms in the study that it is not currently deploying immersion cooling at scale in its production data centers due to these unresolved issues. The company is, however, collaborating with the industry to research alternative fluids and improve the regulatory profile of immersion cooling technologies.

Beyond CPUs: Implications for AI and HPC​

The published Nature study focuses primarily on cooling chips for general compute (CPUs), not the specialized AI accelerators or GPUs that dominate high-performance computing (HPC) and machine learning workloads. However, the research team is already preparing a follow-up that will analyze the lifecycle ramifications of cooling these more power-dense chips, which are expected to magnify both the sustainability challenges and the benefits of advanced cooling techniques.
Early indications suggest that liquid cooling—especially cold plates and perhaps immersion systems—will be essential for meeting the thermal loads of hyperscale AI infrastructure, with the potential to deliver similar or even greater GHG, water, and energy reductions compared to baseline air cooling.

The Road to Net-Zero: Renewables, Design, and Industry Collaboration​

Perhaps the single most significant insight from the LCA is that decarbonizing the electrical grid is by far the largest lever for reducing data center emissions. Cooling system choice matters, but switching data centers to 100% renewable energy—whether generated on-site or procured off-site—yields an 85–90% reduction in GHGs. Microsoft has set a public goal to fully align its "energy load" with renewable resources, and in locations where local grids lack renewable options, the company acquires equivalent renewable energy certificates elsewhere. This approach mirrors best practices outlined by the United Nations Sustainable Development Goals and aligns with industry-wide carbon neutrality commitments from major cloud providers.
Additionally, Microsoft’s open research repository for LCA tooling stands out as a critical industry-building step. By enabling other cloud operators to plug in their own scenarios and datasets, Microsoft is fostering transparent benchmarking and expediting sector-wide improvements. This open, comparable approach may also support policy makers in crafting more effective environmental regulations by providing baseline data and common methodologies.

Cautions and Limitations: The Need for Context and Transparency​

While the study is a milestone, several important caveats apply:
  • Non-universality: Optimal cooling strategies are site-specific, dependent on local climate, power grid, hardware mix, and regulatory context.
  • Fluid Risk: The use of controversial PFAS fluids in two-phase immersion is a potential Achilles' heel, with regulatory trends pointing toward possible phaseouts.
  • Design Sensitivity: Reported savings are averages and can shift dramatically with different design assumptions. Stakeholders should always cross-validate lifecycle assessments with local, up-to-date data.
  • Operational Complexity: Deploying advanced liquid cooling (immersion, cold plates) comes with maintenance, retrofitting, and supply chain challenges not captured fully in LCA numbers.
The study’s authors are explicit on these points: no single cooling technology is universally “right.” Instead, the value lies in equipping engineers—and decision-makers across the industry—with transparent, robust tools for making context-sensitive decisions.

Critical Analysis: Strengths and Risks​

Notable Strengths​

  • Comprehensive Scope: The LCA moves beyond operational efficiency to address hidden impacts from manufacturing, logistics, and disposal, offering a truly holistic footprint.
  • Industry Openness: Microsoft’s decision to publish its methodology and tooling sets a high standard for corporate responsibility in sustainability research, potentially accelerating sector-wide progress.
  • Quantitative, Verifiable Metrics: Publishing detailed results in a peer-reviewed journal like Nature, and at industry summits (like the Open Compute Project Global Summit), ensures methodological rigor and transparency.

Potential Risks​

  • Reliability of Underlying Assumptions: As with all complex models, changing variables in energy supply, fluid sources, or local policies may yield markedly different environmental profiles.
  • Regulatory Uncertainty: Heavy reliance on substances such as PFAS in advanced cooling introduces significant regulatory and reputational risks for cloud operators.
  • Limited Application: The study currently does not cover AI-specific chips, which may exhibit very different power and cooling profiles.

Conclusion: A Blueprint for Greener, Smarter Data Centers​

Microsoft’s Nature study on life cycle assessment for data center cooling is, by multiple accounts, a landmark contribution to the field of sustainable cloud infrastructure. Quantifying, rather than assuming, the true costs—across energy, water, and carbon—enables more effective, transparent decision-making, both within Microsoft and across the broader technology sector.
Key takeaways include the substantial GHG and water savings possible with cold plate and immersion cooling (though immersion faces clear regulatory hurdles), the overriding impact of sourcing renewable energy, and the power of industry-wide tools for apples-to-apples comparison. As demand for cloud computing continues its rapid climb—driven by artificial intelligence, edge computing, and digital transformation—the approaches exemplified here will be indispensable.
Moving forward, industry stakeholders would do well to leverage Microsoft’s open repository, validate findings in their own operational contexts, and prioritize transparent, forward-looking sustainability metrics in all phases of data center life. In the evolving quest for a greener cloud, such cradle-to-grave assessments are not just helpful—they are essential.

Source: Microsoft Microsoft quantifies environmental impacts of datacenter cooling from ‘cradle to grave’ in new Nature study
 